bonjour a tous,

si une âme charitable peu m’aider un peu…

voici le topo, j’ai acheter, [IPX800V4](https://gce-electronics.com/1483-.html)( j’ai pas la [V3](https://gce-electronics.com/57-.html)),[X200PH](https://gce-electronics.com/839-.html),[Xbridge](https://gce-electronics.com/1078-.html), et filtre pour [X-200PH](https://gce-electronics.com/839-.html), sondes, solutions étalonsPH-RX, sonde tc100,[X-thl](https://gce-electronics.com/1266-.html).  
premiere question, me manque t’il quelque chose ?([IPX800V3](https://gce-electronics.com/57-.html) ou X400ana)

pour la connexion, j’ai suivi celle de @fgtoul du 5 septembre sur le forum et j’ai ajouté l’alimentation 12V sur le [xbridge](https://gce-electronics.com/1078-.html) si-non pas d’allumage du [X200PH](https://gce-electronics.com/839-.html)

pour la configuration dans l’ipx je ne trouve rien pour m’aider.

firmware 35=ok  
connexion dynsdns=ok  
tc100=ok  
[X-thl](https://gce-electronics.com/1266-.html)=ok

---

<div class="post-metadata">

**Author:** ![fgtoul](https://forum.gce-electronics.com/user_avatar/forum.gce-electronics.com/fgtoul/32/28801_2.png) [@fgtoul](https://forum.gce-electronics.com/u/fgtoul)\
**Post date:** [Mars 16, 2018, 5:58 UTC](https://forum.gce-electronics.com/t/connexion-configuration-ipx800v4-et-x200ph/6533/2 "2018-03-16T05:58:43Z")

</div>

Bonjour et bienvenu

> [@aquabrass](#):
>
> pour la connexion, j’ai suivi celle de “fgtoul” du 5 septembre sur le forum et j’ai ajouté l’alimentation 12V sur le [xbridge](https://gce-electronics.com/1078-.html) si-non pas d’allumage du [X200PH](https://gce-electronics.com/839-.html).

(pour mentionner quelqu’un, vous pouvez utiliser @ devant le nom. L’utilisateur reçoit une notification. J’ai corrigé votre message.)

le schéma initial concernait une [IPX800V3](https://gce-electronics.com/57-.html) qui alimente directement la [X200PH](https://gce-electronics.com/839-.html) via la bretelle RJ12. En transposant avec une [IPX800 V4](https://gce-electronics.com/1483-.html) et un [x-bridge](https://gce-electronics.com/1078-.html), il faut effectivement amener 12V au [X-Bridge](https://gce-electronics.com/1078-.html).  
Par contre, le câblage représentait des fonction **ET OU** en connectant des relais en série ou en parallèle. Avec l’[IPX800 V4](https://gce-electronics.com/1483-.html), tout se fait dans les scènes, vous n’avez donc pas besoin de ce type de câblage, ça vous permet d’économiser des relais et de les utiliser à d’autres fonctions.

voici un schéma de connexion avec [x-bridge](https://gce-electronics.com/1078-.html) et filtre :

> [@Regulation piscine / PH-ORP X200Ph](https://forum.gce-electronics.com/t/regulation-piscine-ph-orp-x200ph/4744/56):
>
> Bonjour, Voici un exemple de branchements : cdt

> [@aquabrass](#):
>
> premiere question, me manque t’il quelque chose ?([IPX800V3](https://gce-electronics.com/57-.html) ou X400ana)

ça dépend, vous voulez quoi de plus ? si c’est pour le pH et ORP, vous n’avez besoin de rien d’autre..

> [@aquabrass](#):
>
> pour la configuration dans l’ipx je ne trouve rien pour m’aider.

vous devez récupérer vos valeurs PH et ORP dans des analogiques virtuelles (doc [x-bridge](https://gce-electronics.com/1078-.html)).

 ![image](https://forum.gce-electronics.com/uploads/default/original/2X/8/8b9125aaef1981cefe97a81166540b960ebce06e.png)

Pour la configuration des 2 analogiques virtuelles, vous devez renseigner une formule :  
**_Analogue \> Valeur_**  
X / 100 pour la [X200](https://gce-electronics.com/839-.html) PH  
X - 2500 pour la [X200](https://gce-electronics.com/839-.html) ORP

**_Valeur \> Analogue_**  
X \* 100 pour la [X200](https://gce-electronics.com/839-.html) PH  
X + 2500 pour la [X200](https://gce-electronics.com/839-.html) ORP

plus de précisions ici :

> **[Formules de calcul](https://helpdesk.gce-electronics.com/knowledgebase.php?article=39)**

**Pour la régulation** , vous devrez écrire des scènes utilisant ces analogiques virtuelles en fixant un seuil haut et un seuil bas. Si vous voulez une action sur franchissement du seuil bas, n’oubliez pas d’utiliser «&nbsp; **NON** &nbsp;» «&nbsp; **Analogique virtuelle** &nbsp;» dans l’évènement du scénario.

PS : j’ai renommé votre sujet, car la compatibilité [X-200PH](https://gce-electronics.com/839-.html) / [IPX800V4](https://gce-electronics.com/1483-.html) n’est pas en cause  
cdt

---

<div class="post-metadata">

**Author:** ![aquabrass](https://forum.gce-electronics.com/letter_avatar_proxy/v4/letter/a/5daacb/32.png) [@aquabrass](https://forum.gce-electronics.com/u/aquabrass)\
**Post date:** [Mars 16, 2018, 7:45 UTC](https://forum.gce-electronics.com/t/connexion-configuration-ipx800v4-et-x200ph/6533/3 "2018-03-16T07:45:21Z")

</div>

Bonjour,

Et la lumière fut …

100% ok maintenant

Un grand merci !

---

<div class="post-metadata">

**Author:** ![Shime\_14](https://forum.gce-electronics.com/letter_avatar_proxy/v4/letter/s/d26b3c/32.png) [@Shime\_14](https://forum.gce-electronics.com/u/Shime_14)\
**Post date:** [Mars 21, 2020, 7:26 UTC](https://forum.gce-electronics.com/t/connexion-configuration-ipx800v4-et-x200ph/6533/4 "2020-03-21T19:26:28Z")

</div>

Salut,

Dans le tableau tu indiques que 1-2 c’est entrer analogique virtuelles 29 et 30 mais j’ai pas les même valeur dans 29 que dans 30

La dans 29 est plus au moins correct 7.5 (elle varie beaucoup entrer 7.5 et 8 (je sais pas si c’est normal)) bref et dans 30 j’ai entrer 29 et 31.

29 :

 ![image](https://forum.gce-electronics.com/uploads/default/original/2X/4/4b12916a5125f418bc0bcec49978d1ae2f64e3af.png)

30:

 ![image](https://forum.gce-electronics.com/uploads/default/original/2X/c/cedb90d663fa0d184ea1348d1715bcced4c4625b.png)

Merci

cdt

---

<div class="post-metadata">

**Author:** ![fgtoul](https://forum.gce-electronics.com/user_avatar/forum.gce-electronics.com/fgtoul/32/28801_2.png) [@fgtoul](https://forum.gce-electronics.com/u/fgtoul)\
**Post date:** [Mars 21, 2020, 8:08 UTC](https://forum.gce-electronics.com/t/connexion-configuration-ipx800v4-et-x200ph/6533/5 "2020-03-21T20:08:06Z")

</div>

Bonjour ,  
Je confirme les tableaux ci-dessus.

Le port P2 n’est pas prévu pour une sonde PH mais pour une sonde Redox (ORP). D’ailleurs votre jauge n°2 va de 0 à 700, car le redox est en mV.

Pour la valeur PH en P1 (entrée analogique virtuelle 29 dans votre cas) qui fluctue beaucoup, il y a possibilité d’intercaler un filtre qui évitera ce problème dû aux courants vagabonds dans le bassin.

[Le filtre est disponible ici, sur le site GCE](http://gce-electronics.com/fr/ipx800-v4/1381-filtre-x-200ph.html)

cdt

---

<div class="post-metadata">

**Author:** ![Shime\_14](https://forum.gce-electronics.com/letter_avatar_proxy/v4/letter/s/d26b3c/32.png) [@Shime\_14](https://forum.gce-electronics.com/u/Shime_14)\
**Post date:** [Mars 21, 2020, 9:21 UTC](https://forum.gce-electronics.com/t/connexion-configuration-ipx800v4-et-x200ph/6533/6 "2020-03-21T21:21:23Z")

</div>

Pour les sondes ok, une pH brancher sur P1 et une ORP brancher sur P2. Les lumières 1 et 2 sur du [x200PH](https://gce-electronics.com/839-.html) sont allumé mais pas les lumières 3-4 (je sais pas si la sonde n’est pas reconnue ou si je dois mettre un autre fils ou bien si je dois lui faire un calibrage). Ensuite second problème c’est quand suivant le tableau plus haut je suis un peu perdu. Je ne sais pas à quoi correspond dans la section positionnement 1-2 3-4. Et le fait de mettre deux entrée analogique virtuelles me mets le doute. 29 j’ai compris c’est pour le pH. Mais 30 je sais pas si c’est l’ORP ou bien si c’est 31 ou 32 bref un peu la galère pour cette sonde ORP… En tout cas pour l’intant je n’ai pas de 3 et 4 allumer en vers pour ma sonde ORP.

 ![image](https://forum.gce-electronics.com/uploads/default/original/2X/f/f21182c611fc55cfdd684de7dfcbd927afd6c3be.jpeg)

En tout cas merci du conseil pour le filtre je vais me le procuré au plus tôt !

Bonne soirée

---

<div class="post-metadata">

**Author:** ![fgtoul](https://forum.gce-electronics.com/user_avatar/forum.gce-electronics.com/fgtoul/32/28801_2.png) [@fgtoul](https://forum.gce-electronics.com/u/fgtoul)\
**Post date:** [Mars 21, 2020, 11:43 UTC](https://forum.gce-electronics.com/t/connexion-configuration-ipx800v4-et-x200ph/6533/7 "2020-03-21T23:43:30Z")

</div>

Les leds ne correspondent pas aux sondes mais au positionnement de l’extension (canaux utilisés) :

- Les leds 1 et 2 allumées signifient que vous êtes en positionnement 1-2 (canal 1).
- les leds 3 et 4 éteintes, c’est normal. Elles seraient allumées si vous étiez en positionnement 3-4 (canal 2).

Donc si vous êtes en canal 1, alors PH = entrée analogique virtuelle 29 et ORP=entrée analogique virtuelle 30.

Vérifiez si vous avez bien mis vos formules sur les analogiques virtuelles 29 et 30, conformément à la doc du [X-Bridge](https://gce-electronics.com/1078-.html) :

**analogique virtuelle 29 :**  
analogue → valeur : **X / 100**  
valeur-\> analogue ; **X \* 100**

**analogique virtuelle 30 :**  
analogue → valeur : **X - 2500**  
valeur-\> analogue ; **X + 2500**

Votre widget pour la sonde ORP est faux (titre et unité).  
il devrait ressembler à ceci :

 ![image](https://forum.gce-electronics.com/uploads/default/original/2X/8/81b00a4735dbec364cd4b34833f4d126f385cba1.png)